It looks like the piping is dirty... you can use wet vacuum to suck the water from pipe end (normally located in your toilet)... at the same time, ask your friend to pour warm water from the pipe at your fan coil unit (FCU).

I had this problem before (my old aircon)... pipe is dirty (a lot of gel kind of things)...
one time, i had a choked piping... so the condensed water cannot flow.

and it was late, so difficult to get serviceman at that hr.

I found some drain-declog and carefully pour in the drainage... and after a while, a lot of 'junk' flowed out at the other end!