Air conditioning - Any recommendations please??

Status
Not open for further replies.

zellhwang

Member
Joined
Feb 9, 2003
Messages
250
Reaction score
0
Hi Joevyis,

I probably won't stick to Toshiba, since, as mentioned by other forumers, Daikin is the only option for R22 in the current market.

Did you consider to change your compressor to another brands or just stick with Toshiba?
Only can choose the compressor which using R22 if you want to re-use piping.
 

zellhwang

Member
Joined
Feb 9, 2003
Messages
250
Reaction score
0
Hi Jason,

Thanks for the detailed explanation.

My situation is slightly different. After 2-3 hours, it will trip. And when I switch on, it can last for a few minutes before tripping again (not immediately, so I don't think it is condensation).

I actually tried using my vacuum cleaner to do some clean up on the fins of the compressor. After cleaning, it did not trip throughout the night (10-11 hours of operation) for the past 2 nights. This was rather puzzling, as I didn't suspect that dusty fins can cause the compressor to overheat. I have arranged for an aircon technician, but made a cancellation of appointment as the compressor didn't trip for the past 2 nights.

Since it rained today, I also sprayed the fins with water and will continue to monitor for the next few days. If it trips again I will probably change the compressor. My preference is to just change the compressor to minimise the amount of disruptions and mess at home.

Last but not least, you mentioned about 'compatible brand'. From the suggestions of forumers, it seems like Daikin is the only option. Can I use a Daikin compressor (R22) with my current Toshiba blowers ?

Thanks. :)

Hello Zellhwang,

Are you able to switch on the aircon again without tripping say after a few hours or 1 day later? Then the cycle repeats afer itself (2-3 hours trip then afterwhich will continuously trip once you switch on)?

Otherwise is your aircon tripping every single time you on it now?

If it is the former, chances are condensation formed after 2-3 hours of operation and the condensation has hit a wiring/part and caused a trip to happen. Afterwhich it will continue to trip until the wet area dries up and you are able to restart your unit again without tripping. However the cycle will repeat itself after running the system for some time as condensation will form again.

If it is the latter, chances are some parts have shorted out and needs to be checked.

Both scenarios, the trip could be caused by any part and not only restricted to the outdoor unit (compressor). I would suggest that you have your contractor do a check to determine the actual cause so as not to replace the wrong part.

If you are looking at reuse of pipings running on R22 and if you are relatively sure that your pipings are not facing as gas leakage or sweating insualtion problem, for safety measures you can stick back to R-22 system which is as what fellow forumer Terumo have mentioned, Dakin.

Otherwise, if you are changing into a new system running on R410, best that you have the proper flushing procedures done so as not to cause damage to your system.

Alternatively, you can also look into compressor replacement however the price might not be cost efficient. (Replacement can be with an Original Toshiba of the same model or a compatible brand).

Best that you have your contractor do a check to determine the cause of fault first and get a quotation on the repair/replacement before considering your possibilities.

My take is that if your system have been constantly giving you problems and the fault this time after checking lies in the compressor, I would consider to change to a whole new system completely for a peace of mind.

Hope this helps.

Best Regards,

Jason Tham
 

zellhwang

Member
Joined
Feb 9, 2003
Messages
250
Reaction score
0
Hi mrairc,

I am not sure how to check the air con MCB. If aircon MCB is underrated, MCB should trip instead of RCCB?

The trip was at RCCB, which has a label "40A DP 30mA". I have not clues about MCB stuffs... :(

First check your air con MCB is using 20 amp or not . coz old molde RCCB many using 15 amp for air con . I come a cross sometime is the MCB or RCCB is fault . :)
 

terumo

Senior Member
Joined
Oct 20, 2004
Messages
1,908
Reaction score
1
To Zellhwang,

If ur Toshiba is non inverter, then Daikin outdoor can work but warranty wise, I duh tink Daikin will cover. Cos indoor unit is different brands.

Or u can also consider reconditioned outdoor if u do not wish to replace ur indoor units & piping.
 

maxicoolservices

Suspended
Joined
Apr 11, 2013
Messages
359
Reaction score
0
Hello Zellhwang,

I believe what you meant was cleaning up the coils/fins at the condenser.

When the coils/fins at the condenser are dirty/dusty, the hot air cannot be emitted properly from the condenser and might cause a short cycle and lead to an overload trip. Overtime, with the heat building up inside, it might cause the condenser to malfunction.

There are actually several options depending on what is the actual fault cause part.

Say if the compressor is diagnosed to be faulty, you can opt to change only the compressor with an original Toshiba compressor or equivalent brand(btw the outdoor unit is called the condenser and the compressor is a part inside the condenser. Inside the condenser hosts other parts such as pcb boards etc).

Another would be to change the whole condenser and yes since your system is a non inverter, Daikin will match your indoor Toshiba blowers. This works for non-inverter systems only.

Since the cleaning, the condenser has been working well without trip so it would most probably be the best to monitor the situation as what you are doing.

If the trip does happen again, it would be best you have your contractor come down for a check as it would most likely be a short on some parts be it internal or external. With the actual fault diagnosed, it would then be easier for you to gauge which option would be the most cost savings and least disruption caused to your premises so as not to affect your baby.


Best Regards,

Jason Tham


Hi Jason,

Thanks for the detailed explanation.

My situation is slightly different. After 2-3 hours, it will trip. And when I switch on, it can last for a few minutes before tripping again (not immediately, so I don't think it is condensation).

I actually tried using my vacuum cleaner to do some clean up on the fins of the compressor. After cleaning, it did not trip throughout the night (10-11 hours of operation) for the past 2 nights. This was rather puzzling, as I didn't suspect that dusty fins can cause the compressor to overheat. I have arranged for an aircon technician, but made a cancellation of appointment as the compressor didn't trip for the past 2 nights.

Since it rained today, I also sprayed the fins with water and will continue to monitor for the next few days. If it trips again I will probably change the compressor. My preference is to just change the compressor to minimise the amount of disruptions and mess at home.

Last but not least, you mentioned about 'compatible brand'. From the suggestions of forumers, it seems like Daikin is the only option. Can I use a Daikin compressor (R22) with my current Toshiba blowers ?

Thanks. :)
 

Kiajoon

Master Member
Joined
Sep 9, 2000
Messages
2,648
Reaction score
0
Hi all

I used Time Wing services over the weekend (Sunday) for a urgent leak problem. They called and came half an hour early.

The experienced technician also advised upon how to minimise my problem, giving me a 'mini' lesson on good AC operation method.

Charges were reasonable considering it is only 1 unit to service on this visit.
 

zellhwang

Member
Joined
Feb 9, 2003
Messages
250
Reaction score
0
Hi terumo,

Yes, its non-inverter. Good to hear that Daikin can work, at least I have an option. I would prefer not to use reconditioned units. Anyway, after cleaning my condenser with vacuum cleaner and water spray, the trip didn't happen for the past 4 nights. Hopefully I won't have to change the condenser that soon. :) Thanks.

To Zellhwang,

If ur Toshiba is non inverter, then Daikin outdoor can work but warranty wise, I duh tink Daikin will cover. Cos indoor unit is different brands.

Or u can also consider reconditioned outdoor if u do not wish to replace ur indoor units & piping.
 

zellhwang

Member
Joined
Feb 9, 2003
Messages
250
Reaction score
0
Hi Jason,

Yes, I got the term wrong. I cleaned up the coils/fins of the condenser. So far, it has not tripped for the past 4 nights, so I would assume that it is due to dirt/dust and overheating. If the trip happens again, I will get the technician to come down for a check.

It is good that managed to get all the answers I needed here. Thanks for the help. :)



Hello Zellhwang,

I believe what you meant was cleaning up the coils/fins at the condenser.

When the coils/fins at the condenser are dirty/dusty, the hot air cannot be emitted properly from the condenser and might cause a short cycle and lead to an overload trip. Overtime, with the heat building up inside, it might cause the condenser to malfunction.

There are actually several options depending on what is the actual fault cause part.

Say if the compressor is diagnosed to be faulty, you can opt to change only the compressor with an original Toshiba compressor or equivalent brand(btw the outdoor unit is called the condenser and the compressor is a part inside the condenser. Inside the condenser hosts other parts such as pcb boards etc).

Another would be to change the whole condenser and yes since your system is a non inverter, Daikin will match your indoor Toshiba blowers. This works for non-inverter systems only.

Since the cleaning, the condenser has been working well without trip so it would most probably be the best to monitor the situation as what you are doing.

If the trip does happen again, it would be best you have your contractor come down for a check as it would most likely be a short on some parts be it internal or external. With the actual fault diagnosed, it would then be easier for you to gauge which option would be the most cost savings and least disruption caused to your premises so as not to affect your baby.


Best Regards,

Jason Tham
 

lexliz7

Junior Member
Joined
Apr 9, 2014
Messages
6
Reaction score
0
Kimura Aircon

Hi got this Japanese brand Kimura installed. Nice looking n smaller in size compared to other brands.cute!! Has interesting features like Haze Eliminator,energy saving and self clean. Good price from Supreme Aircon. really cool..
 

Akai Ryu

Arch-Supremacy Member
Joined
Dec 14, 2007
Messages
21,516
Reaction score
25
Anyone got feedback on gain city ac cleaning service? Or other ac cleaning recommendation?
 

lexliz7

Junior Member
Joined
Apr 9, 2014
Messages
6
Reaction score
0
Anyone using KIMURA Japanese brand aircon?

Care to share? Any review?

Hi i bought Kimura. Would say its very good. Cooling is very good and quiet n has temperature display.Overall just as good as any top brands. It's cheaper though.
 

sky1234

Junior Member
Joined
Apr 9, 2014
Messages
1
Reaction score
0
How about portable aircons. Anyone has experience? Thinking to get from Giant at $580. I need one for a small room about 10ft x 16ft.
 

nwy42

Senior Member
Joined
Jun 24, 2003
Messages
1,369
Reaction score
0
I jus dont want those that only want to change or top up "gas" to make quick buck

pm me . colleague intro me one. but i have not used. get those who do it themself kind of business. gain city.. errm not sure no comments
 

tubbycub

Junior Member
Joined
Oct 31, 2000
Messages
88
Reaction score
0
Hi everyone, I am planning to get aircon for my parent's place which is a 30 year old 3A HDB. I have learnt quite a lot of about aircon in this thread, thanks to the gurus. Based on what I have gathered so far, I think the ME inverter system 2 (starmex?) is the best choice as I am looking for cost savings and ease of maintenance.

Regarding installation workmanship and who to buy from, I haven't seen much recommendations posted here, maybe it is not allowed. I saw that many here buy from GC but the reviews were mixed. So can anyone recommend which dealer should I buy from and can provide good installation?

Thanks.
 

Jenjovstan

Junior Member
Joined
Apr 9, 2014
Messages
19
Reaction score
0
I've got my installation done by Eighteen Degree Aircon Svcs. Good, reasonable & reliable.