Hi I am deciding whether to buy daikin ismile (R410) or ismile eco (R32) series air con. Is for my new resale flat that is 5 years old. This will probably not be my last house. We are having a dilemma in choosing which to get .
1) If buy R410 now , the next time that I need to repair probably 5 years later will the spare parts be rare to find or costly since Singapore government going to ban selling of R410 air con therefore parts are going to be limited.

2) if I buy R32 will it be quite unstable cause is only in the market for less than 6 months , few installers said that is new can be unstable and R32 is flammable.
And the spare parts now is more expensive that R410 because majority of people are using R410.

Any advice is greatly appreciated!
https://www.daikin.com/corporate/why_daikin/glance/modals/07_R32/
any more hesitation?
 

sleow003

Junior Member
Joined
Aug 11, 2015
Messages
8
Reaction score
0
Hahas thanks for the sharing ! Because I can’t seem to find review about daikin air con. Contractor kept saying that ismile eco is the very first version so will have a lot of problem unlike ismile air con which have been around for sometime already.
 

wacko

Arch-Supremacy Member
Deluxe Member
Joined
Jan 1, 2000
Messages
15,400
Reaction score
198
first to be distributed in Singapore, and Singapore is a late adopter for R32 (for whatever reasons). so I reckon hardware wise Daikin has already gone through several years of manufacturing experience. Service personnel wise will be the concern, but there is little difference in the operating mechanism of a R32 aircon vs a R410A aircon, so I wouldn't be too worried about that.
 

sleow003

Junior Member
Joined
Aug 11, 2015
Messages
8
Reaction score
0
Okay thanks for the advise . Likely I will be going for ismile eco, but hope can get it during promotion hahas . Cause the extended warranty promotion expired.
 
Joined
Apr 19, 2018
Messages
462
Reaction score
34
My new flat is similar to new BTO.
Kitchen, Living room and small walkway to bed rooms.
No doors or partition between these 3 areas

I want to get aircon for living room but only need to cool living room area.

Sizes of Room and BTU according to https://www.e2singapore.gov.sg/over...y-at-home/sizing-your-air-conditioning-system

Bedroom 1: 12 sqm, 8200 BTU/hr
Bedroom 2: 11 sqm, 7500 BTU/hr
Bedroom 3: 13.5 sqm, 9200 BTU/hr
Living room (Including Walkway): 29.3 sqm, 20000 BTU/hr
Living room (Excluding Walkway): 25sqm, 17000 BTU/hr

How to calculate aircon BTU needed for my living room? Do I need to include area of walkway and kitchen?
The previous owner is using thicker insulation, can the insulation be reused?
Thinking of getting this set:
MITSUBISHI ELECTRIC SYSTEM 4- MXY4G33VA2 (36500 BTU/hr) / MSXYFN10VE x 3 (9000 BTU/hr) / MSXYFN18VE (18000 BTU/hr)


I understand can only on either 3 bedrooms or 1 living room + 2 bedrooms
 
Last edited:

GBC

High Supremacy Member
Joined
Jan 1, 2000
Messages
25,625
Reaction score
4,322
My new flat is similar to new BTO.
Kitchen, Living room and small walkway to bed rooms.
No doors or partition between these 3 areas

I want to get aircon for living room but only need to cool living room area.

Sizes of Room and BTU according to https://www.e2singapore.gov.sg/over...y-at-home/sizing-your-air-conditioning-system

Bedroom 1: 12 sqm, 8200 BTU/hr
Bedroom 2: 11 sqm, 7500 BTU/hr
Bedroom 3: 13.5 sqm, 9200 BTU/hr
Living room (Including Walkway): 29.3 sqm, 20000 BTU/hr
Living room (Excluding Walkway): 25sqm, 17000 BTU/hr

How to calculate aircon BTU needed for my living room? Do I need to include area of walkway and kitchen?
The previous owner is using thicker insulation, can the insulation be reused?
Thinking of getting this set:
MITSUBISHI ELECTRIC SYSTEM 4- MXY4G33VA2 (36500 BTU/hr) / MSXYFN10VE x 3 (9000 BTU/hr) / MSXYFN18VE (18000 BTU/hr)


I understand can only on either 3 bedrooms or 1 living room + 2 bedrooms

MXY4G33VA2 normal rating is only 22,500 BTU, so can only on either 2 x MSXYFN10VE or 1 x MSXYFN18VE.
 

Ark Law

Arch-Supremacy Member
Joined
Jan 29, 2013
Messages
11,540
Reaction score
495
Thinking of getting this set:
MITSUBISHI ELECTRIC SYSTEM 4- MXY4G33VA2 (36500 BTU/hr) / MSXYFN10VE x 3 (9000 BTU/hr) / MSXYFN18VE (18000 BTU/hr)


I understand can only on either 3 bedrooms or 1 living room + 2 bedrooms

4G33VA2 is only rated at 22.5K BTU, and with your combination selection, rated at 21.1K BTU.

Even if only switch on 1LR (1x FN18) + 2BR (2x FN10), your effective output is only 9.9K BTU for living room and 5.5K BTU for each bedroom
 
Joined
Apr 19, 2018
Messages
462
Reaction score
34
MXY4G33VA2 normal rating is only 22,500 BTU, so can only on either 2 x MSXYFN10VE or 1 x MSXYFN18VE.
4G33VA2 is only rated at 22.5K BTU, and with your combination selection, rated at 21.1K BTU.

Even if only switch on 1LR (1x FN18) + 2BR (2x FN10), your effective output is only 9.9K BTU for living room and 5.5K BTU for each bedroom

Thanks... so what configuration would you guys recommend?

I think the maximum air-con we will on is 1 LR + 1 BR for now.
Unless got kids then maybe increase to 1 LR + 2 BR.

But it's only if there are guests in our house (which will be rare). If not, the max we would on is 2/3 BR only.
 

batniss

Arch-Supremacy Member
Joined
Nov 23, 2015
Messages
16,184
Reaction score
413
Thanks... so what configuration would you guys recommend?

I think the maximum air-con we will on is 1 LR + 1 BR for now.
Unless got kids then maybe increase to 1 LR + 2 BR.

But it's only if there are guests in our house (which will be rare). If not, the max we would on is 2/3 BR only.
upgrade your output unit.
 

Ark Law

Arch-Supremacy Member
Joined
Jan 29, 2013
Messages
11,540
Reaction score
495
Thanks... so what configuration would you guys recommend?

I think the maximum air-con we will on is 1 LR + 1 BR for now.
Unless got kids then maybe increase to 1 LR + 2 BR.

But it's only if there are guests in our house (which will be rare). If not, the max we would on is 2/3 BR only.
If you want more cooling capacity, the only option is to top-up to the 4G38VA2 / 5G48VA2 condenser.

Performance for 4G33VA2:
LR only: 17K BTU
LR + 1BR: 13.5K + 7.6K
LR + 2BR: 9.9K + 5.5K per BR
LR + 3BR: 7.8K + 4.4K per BR

Performance for 4G38VA2:
LR only: 17K BTU
LR + 1BR: 15.3K + 9.5K
LR + 2BR: 11.2k + 6.3K per BR
LR + 3BR: 8.9K + 4.9K per BR

Your other alternative is to opt for 2 condenser setup, 1x sys1 (GN24VA) + 1x sys3 (3G28VA2):
LR only: 22.5K BTU
LR + 1BR: 22.5K + 9.5K
LR + 2BR: 22.5K + 9.5K per BR
LR + 3BR: 22.5K + 6.4K per BR

This 2 condenser setup is similar to my own home, where I have a single split for LR, and a sys3 for 3 BRs, of which only 2 BRs are used daily
 
Joined
Apr 19, 2018
Messages
462
Reaction score
34
If you want more cooling capacity, the only option is to top-up to the 4G38VA2 / 5G48VA2 condenser.

Performance for 4G33VA2:
LR only: 17K BTU
LR + 1BR: 13.5K + 7.6K
LR + 2BR: 9.9K + 5.5K per BR
LR + 3BR: 7.8K + 4.4K per BR

Performance for 4G38VA2:
LR only: 17K BTU
LR + 1BR: 15.3K + 9.5K
LR + 2BR: 11.2k + 6.3K per BR
LR + 3BR: 8.9K + 4.9K per BR

Your other alternative is to opt for 2 condenser setup, 1x sys1 (GN24VA) + 1x sys3 (3G28VA2):
LR only: 22.5K BTU
LR + 1BR: 22.5K + 9.5K
LR + 2BR: 22.5K + 9.5K per BR
LR + 3BR: 22.5K + 6.4K per BR

This 2 condenser setup is similar to my own home, where I have a single split for LR, and a sys3 for 3 BRs, of which only 2 BRs are used daily
Thank you so much for the explanation.

The 2 condenser setup costs around $5.4k
4G33VA2: $4.47k
4G38VA2: $4.95k
 

GBC

High Supremacy Member
Joined
Jan 1, 2000
Messages
25,625
Reaction score
4,322
If you want more cooling capacity, the only option is to top-up to the 4G38VA2 / 5G48VA2 condenser.

Performance for 4G33VA2:
LR only: 17K BTU
LR + 1BR: 13.5K + 7.6K
LR + 2BR: 9.9K + 5.5K per BR
LR + 3BR: 7.8K + 4.4K per BR

Performance for 4G38VA2:
LR only: 17K BTU
LR + 1BR: 15.3K + 9.5K
LR + 2BR: 11.2k + 6.3K per BR
LR + 3BR: 8.9K + 4.9K per BR

Your other alternative is to opt for 2 condenser setup, 1x sys1 (GN24VA) + 1x sys3 (3G28VA2):
LR only: 22.5K BTU
LR + 1BR: 22.5K + 9.5K
LR + 2BR: 22.5K + 9.5K per BR
LR + 3BR: 22.5K + 6.4K per BR

This 2 condenser setup is similar to my own home, where I have a single split for LR, and a sys3 for 3 BRs, of which only 2 BRs are used daily
If only need MSXYFN18VE which is 17,060 btu for LR, a system 1 MSY-GN18VA (16,378 btu) should be sufficient.
For the other 3 bedroom using MSXYFN10VE (9,550 btu each , 28,650 btu in total), MXY-3G28VA2 will only give you 20,500 btu while MXY-4G38VA2 give you 25,200 btu.
MXY-3G28VA2 will give you 6,483 btu per room
MXY-4G38VA2 will give you 7,950 btu per room.

So I think 1 x system 1 MSY-GN18VA for LR + 1 x system 4 MXY-4G38VA2 for the other 3 bedrooms is a better choice.
 

Ark Law

Arch-Supremacy Member
Joined
Jan 29, 2013
Messages
11,540
Reaction score
495
If only need MSXYFN18VE which is 17,060 btu for LR, a system 1 MSY-GN18VA (16,378 btu) should be sufficient.
For the other 3 bedroom using MSXYFN10VE (9,550 btu each , 28,650 btu in total), MXY-3G28VA2 will only give you 20,500 btu while MXY-4G38VA2 give you 25,200 btu.
MXY-3G28VA2 will give you 6,483 btu per room
MXY-4G38VA2 will give you 7,950 btu per room.

So I think 1 x system 1 MSY-GN18VA for LR + 1 x system 4 MXY-4G38VA2 for the other 3 bedrooms is a better choice.

Only reason I suggested 3G28VA2 is because the savings between 28VA2 and 38VA2 is considerable enough for a reasonable compromise for when they run the 3rd BR FCU on rare occasions. The 3G28VA2 is still able to supply the 2x BR's FN10s at full capacity.

Still, I wish ME continued having the 2-tick range. The stupidity of chasing 5-ticks while compromising cooling capacity AND charging more is nothing more than an easy money grab by ME. The old 2-tick entry level 3A28VA (25.5K) has more capacity than the 4G38VA2 (25.2K). Combined with crappy aircon salesmen, we get the mess that we have today.

Thank you so much for the explanation.

The 2 condenser setup costs around $5.4k
4G33VA2: $4.47k
4G38VA2: $4.95k
Yep. Prices based on GC:
4G38VA2 (sys3) + GN18VA - $6240
3G28VA2 (sys3) + GN18VA - $5430
3G28VA2 (sys3) + GN24VA - $5670
4G33VA2 (sys4) - $4380
4G38VA2 (sys4) - $4960

Though you could scout other aircon contractors. I remember mine quoting me $1.8k for GN24
 
Joined
Apr 19, 2018
Messages
462
Reaction score
34
Only reason I suggested 3G28VA2 is because the savings between 28VA2 and 38VA2 is considerable enough for a reasonable compromise for when they run the 3rd BR FCU on rare occasions. The 3G28VA2 is still able to supply the 2x BR's FN10s at full capacity.

Still, I wish ME continued having the 2-tick range. The stupidity of chasing 5-ticks while compromising cooling capacity AND charging more is nothing more than an easy money grab by ME. The old 2-tick entry level 3A28VA (25.5K) has more capacity than the 4G38VA2 (25.2K). Combined with crappy aircon salesmen, we get the mess that we have today.


Yep. Prices based on GC:
4G38VA2 (sys3) + GN18VA - $6240
3G28VA2 (sys3) + GN18VA - $5430
3G28VA2 (sys3) + GN24VA - $5670
4G33VA2 (sys4) - $4380
4G38VA2 (sys4) - $4960

Though you could scout other aircon contractors. I remember mine quoting me $1.8k for GN24
Didn't know choosing aircon is so complicated.

Now really have to think if I will ever use all the aircon at the same time. And even if I do, will the reduced cooling be enough? Or will it just take a longer time to cool down the room?
I'm willing to compromise if it just takes a longer time to cooldown. Afterall, I won't switch on all aircon so often unless there are guest at my house.

Also, I think you guys missed out on one of my questions. Appreciate it if you guys can give advice.

My living room is connected to the kitchen and a walkway to the bedrooms. Do I need to account for those areas when calculating the BTU/hr needed?

Area that I need to be cooled: 17.5 sqm
Living room ONLY: 25 sqm
Living room + Walkway: 29 sqm
Living room + Walkway + Kitchen: 39 sqm



Highlighted green is the area that I want to be cooled.
Highlighted red is the area that is walking past only.
Highlighted blue is the location of aircon.
 

batniss

Arch-Supremacy Member
Joined
Nov 23, 2015
Messages
16,184
Reaction score
413
Didn't know choosing aircon is so complicated.

Now really have to think if I will ever use all the aircon at the same time. And even if I do, will the reduced cooling be enough? Or will it just take a longer time to cool down the room?
I'm willing to compromise if it just takes a longer time to cooldown. Afterall, I won't switch on all aircon so often unless there are guest at my house.

Also, I think you guys missed out on one of my questions. Appreciate it if you guys can give advice.

My living room is connected to the kitchen and a walkway to the bedrooms. Do I need to account for those areas when calculating the BTU/hr needed?

Area that I need to be cooled: 17.5 sqm
Living room ONLY: 25 sqm
Living room + Walkway: 29 sqm
Living room + Walkway + Kitchen: 39 sqm



Highlighted green is the area that I want to be cooled.
Highlighted red is the area that is walking past only.
Highlighted blue is the location of aircon.
of course, you need UNLESS it is covered up (with a door, window etc).
 

yahoosoda

Junior Member
Joined
Feb 14, 2009
Messages
91
Reaction score
0
just curious, lets say if my compressor is rated at 6kW, and i only turn on air con for 1 room (9k btu/ 2.6kW), the energy consumption from the wall would it be 6kW or 2.6kW or slightly higher than 2.6kW?
 

wacko

Arch-Supremacy Member
Deluxe Member
Joined
Jan 1, 2000
Messages
15,400
Reaction score
198
just curious, lets say if my compressor is rated at 6kW, and i only turn on air con for 1 room (9k btu/ 2.6kW), the energy consumption from the wall would it be 6kW or 2.6kW or slightly higher than 2.6kW?
don't confuse cooling capacity vs power consumption rate. in any case, the power consumption will be in line with what is being switched on, a compressor doesn't draw max power consumption all the time.
 

GBC

High Supremacy Member
Joined
Jan 1, 2000
Messages
25,625
Reaction score
4,322
just curious, lets say if my compressor is rated at 6kW, and i only turn on air con for 1 room (9k btu/ 2.6kW), the energy consumption from the wall would it be 6kW or 2.6kW or slightly higher than 2.6kW?
Using a MXY-3G28VA2 running MSXYFN10VE for 1 room, the total power input (normal rating) is around 0.62kw. The total energy consumption (simplified computation) would be 0.62kw x the operating hours of the compressor. Where I get the 0.62kw, please refer to the official starmex brochure.
 