Old 03-07-2015, 04:34 PM   #6046
Suspended
 
Join Date: Apr 2013
Posts: 359
Hello item2sell,

Based on description, it is likely the blower/coil of your master bedroom aircon is mouldy hence the musky odor.

If all indoor units are not as cool as before, it could be due to a gas shortage or simply because the indoor units need a cleaning.

The outdoor condenser turning itself on and off does seem to be rather peculiar for inverter system. It would be good to have the unit checked as the condenser is an important part of the airconditioning system.

I would suggest that if you had not serviced your units for the past 6 months to have your contractor do a servicing. The servicing might be able to resolve the musky odor and at the same time your contractor can do a check on the condenser and address the on/off issue.

Best Regards,

Jason Tham

My aircon recently not cooling anymore suddenly. I don't know why.
I only turn on the aircon in the master bedroom. I occasionally on the aircon in my study room. My aircon setting is at 25degree.

Last week, i found that there is a musky smell when i turn on the aircon, and found the aircon is not as cooling as before. but in the morning after i wake up, the air feels cooler, though not as cold as last time.

I try all the other rooms (I have system 3 split mitsubishi electric starmex), and found all the other rooms aircon also not cold as before.

I go to see the outdoor compressor, it seems to turn on and then turn off after a while, then turn on again.

Does anyone has similar encounter before?

Is it gas leak? or compressor spoilt?

Any recommendation for repair contact?
maxicoolservices is offline  
Old 03-07-2015, 04:47 PM   #6047
Junior Member
 
Join Date: Jul 2015
Posts: 2
Aircon for HDB Maisonette

Hi, I would like to ask on the following for EM resale flat:

Requirements:
1. Aircon for living room
2. Aircon for 3 bed rooms upstairs (typically not all will be on at the same time).

Can you all pls advise on the aircon brand and types which I should go for? Should I go for a System 3 + 1? or should I go for system 2 + 2? or just go for System 4?

Thanks a lot!
abcdtan is offline  
Old 03-07-2015, 05:54 PM   #6048
Suspended
 
Join Date: Nov 2008
Posts: 1,690
Hi, I would like to ask on the following for EM resale flat:

Requirements:
1. Aircon for living room
2. Aircon for 3 bed rooms upstairs (typically not all will be on at the same time).

Can you all pls advise on the aircon brand and types which I should go for? Should I go for a System 3 + 1? or should I go for system 2 + 2? or just go for System 4?

Thanks a lot!
Hi, sys 4 still not sufficient at all.
Otherwise go with 2 condenser.

Upper floor with system 3 , 10x2 + 13k master bedroom
Downstay living room with single split 24k or system 3 3A28VA ME Starmex with 13k & 18k split out on dinner & living area.

Just depend how often you usage per day on downstay
kimsim is offline  
Old 03-07-2015, 07:46 PM   #6049
Member
 
Join Date: Jul 2007
Posts: 199
Anyone could recommend a aircon that is good enough for a small room.

No exisiting air-con have been fixed before.

budget well around 1k.
Petslave is offline  
Old 03-07-2015, 11:24 PM   #6050
Junior Member
 
Join Date: Jul 2015
Posts: 2
Hi, sys 4 still not sufficient at all.
Otherwise go with 2 condenser.

Upper floor with system 3 , 10x2 + 13k master bedroom
Downstay living room with single split 24k or system 3 3A28VA ME Starmex with 13k & 18k split out on dinner & living area.

Just depend how often you usage per day on downstay

Kimsim, thanks for your reply.
So you are saying I would have to put 2 separate condensers? System 3 for upstairs and system 1 24k for downstairs? A system 4 wouldn't work at all for 2 levels?
abcdtan is offline  
Old 04-07-2015, 12:24 AM   #6051
Member
 
Join Date: Sep 2004
Posts: 374
I was searching for how much BTU/hr I will need for my rooms. I came across mostly websites from USA that gives charts for recommended BTU/hr for aircons. Can these values be followed for singapore weather ?
Buzztiger is offline  
Old 04-07-2015, 12:46 AM   #6052
Suspended
 
Join Date: Nov 2008
Posts: 1,690
Kimsim, thanks for your reply.
So you are saying I would have to put 2 separate condensers? System 3 for upstairs and system 1 24k for downstairs? A system 4 wouldn't work at all for 2 levels?
System 4 not sufficient for turns on 4 units at same time.
If concern for Sys 4 the only way go with ME starmex 4A38VA and turn on full & without current limitation will do.
kimsim is offline  
Old 04-07-2015, 09:01 PM   #6053
Junior Member
 
Join Date: Oct 2011
Posts: 12
Hi Bros,

Just wan to seek your advices / opinion:

Just last week JUN 2015, I have had Daikin's Inverter System 3 (R-410A 3MKS50ESG + 3X FTKS25DVM) installed in my home.

It is a total revamp (meaning: complete change of old trunking, PVC and copper pipe to G23 with 3/8" insulation).

I have been using it and find that

1) It is not really that cold, meaning the temp is set to 22deg, but 8 hours later in the morning, the temp reader on my room thermometer (from Home-Fix) reads 24.6deg.

& I am not sure if the AC will be able to reach the set temp of 22deg?

2) It takes quite long for the temp to drop (in my case, it take 1 hour to go from 28 to 25deg and then after that it seem to take like ages to try and reach the 22deg mark)

I do not know if this normal for an inverter AC. Previously, have been using daikin's non-inverter FT25GV1 but it had to be replaced after 15 good years.

Oh man, can't say that I am impressed with the current AC. With the previous AC, I need blanket and enjoy the shiok shiok coldness. Right now, I don't really feel the chill.

Do any of you guys encounter similar issues?
Thanks & sry for the long rant!
infedal is offline  
Old 04-07-2015, 09:27 PM   #6054
Suspended
 
Join Date: Nov 2008
Posts: 1,690
Hi Bros,

Just wan to seek your advices / opinion:

Just last week JUN 2015, I have had Daikin's Inverter System 3 (R-410A 3MKS50ESG + 3X FTKS25DVM) installed in my home.

It is a total revamp (meaning: complete change of old trunking, PVC and copper pipe to G23 with 3/8" insulation).

I have been using it and find that

1) It is not really that cold, meaning the temp is set to 22deg, but 8 hours later in the morning, the temp reader on my room thermometer (from Home-Fix) reads 24.6deg.

& I am not sure if the AC will be able to reach the set temp of 22deg?

2) It takes quite long for the temp to drop (in my case, it take 1 hour to go from 28 to 25deg and then after that it seem to take like ages to try and reach the 22deg mark)



I do not know if this normal for an inverter AC. Previously, have been using daikin's non-inverter FT25GV1 but it had to be replaced after 15 good years.

Oh man, can't say that I am impressed with the current AC. With the previous AC, I need blanket and enjoy the shiok shiok coldness. Right now, I don't really feel the chill.

Do any of you guys encounter similar issues?
Thanks & sry for the long rant!
In the 1st place of 3MKS50ESG should be the wrong place to go for 3 bedroom, if the room size is over 3x4m wide will be taken longer time to cooling down.

Actually the S50ESG is = 17k BTU for 3 rooms if turn on at same time would be works as suffer.
From 17k btu / 3 rooms the btu is lesser than 6k then the cooling performance will take longer and draw more power energy than 3MKS75ESG outdoor model.

Anyway try to top up gas to maximum at least 180 high pressure, to help up cooling peak performance only.
kimsim is offline  
Old 04-07-2015, 10:31 PM   #6055
Senior Member
 
Join Date: Mar 2009
Posts: 1,051
Hi Bros,

I am looking to get a new aircon to replace my existing non-inverter aircon.

3x Room : 4.1M(length) x 2.9M(width) x 2.6M(ceiling)
Usage : 9 hours daily, 3 rooms on simultaneously


The specs in bold is my ideal spec, but i think most low cost installers are using the lower specs.

Model : MXY-3A28VA
Fan coil : 3x MSY-GE10VA
Piping : 22 (or 23) SWG Copper
Insulation : 1/2" (or 3/8") ARMAFLEX Insulation (either class 1 or 0)
drainage : 20-25mm (16mm)
warranty : 5 years

Misc : Free dismantle of old aircon
Free installation of aircon
Rewiring : using at least 3C70(outdoor) 3C40 (indoor)
Proper pipe bender for corners for piping
BCA cert for bracket installer
vacuum pump after installation
max G22 copper pipe per FCU (have to find out whats the length)

Installation of stainless steel bracket : ideally below $150

I check the current limit on the compressor is 8.5A, do i need to install a 15A aircon power point? if i have a existing 15A powerpoint for my current aircon, would that be ok?

Looking at cost : $2880 + $150(bracket)

Any experts can advise if i have noted everything that is needed?
darknite84 is offline  
Old 04-07-2015, 10:37 PM   #6056
Junior Member
 
Join Date: Oct 2011
Posts: 12
In the 1st place of 3MKS50ESG should be the wrong place to go for 3 bedroom, if the room size is over 3x4m wide will be taken longer time to cooling down.

Actually the S50ESG is = 17k BTU for 3 rooms if turn on at same time would be works as suffer.
From 17k btu / 3 rooms the btu is lesser than 6k then the cooling performance will take longer and draw more power energy than 3MKS75ESG outdoor model.

Anyway try to top up gas to maximum at least 180 high pressure, to help up cooling peak performance only.
@kimsim,

Thanks for the input. Yes my room size is actually in fact 3x4. However, most of the time, only 2 of the fancoil is active. Still....,air taking their own sweet time to cool down.

Noted and will get Daikin to check / top up gas!
infedal is offline  
Old 04-07-2015, 10:58 PM   #6057
Junior Member
 
Join Date: Jan 2011
Posts: 59
puzzled

hi experts here,

first time installing an air con in my house. wonder which one to install. thinking to install a system 3.

went to bigbox and the promoter suggested LG brand to me over mitsubishi. is LG air con good? the filter inside quality looks 'better' than the mitsubishi catechin filter .
wrongwroks is offline  
Old 04-07-2015, 11:12 PM   #6058
Suspended
 
Join Date: Nov 2008
Posts: 1,690
@kimsim,

Thanks for the input. Yes my room size is actually in fact 3x4. However, most of the time, only 2 of the fancoil is active. Still....,air taking their own sweet time to cool down.

Noted and will get Daikin to check / top up gas!
Usually the installer won't top up for you before they leaved your house, unless you ask then they will simple check.

Inverter R410a gas pressure should have at least 170-180 pressure is shown on the meter for switch on all units at same time.

Otherwise gas is low and taken longer duration time for reaching pre-set temperature also to lower down from 25c to 23c is 30% more energy to compare set to 25C can feel that same result.
kimsim is offline  
Old 04-07-2015, 11:32 PM   #6059
Suspended
 
Join Date: Nov 2008
Posts: 1,690
hi experts here,

first time installing an air con in my house. wonder which one to install. thinking to install a system 3.

went to bigbox and the promoter suggested LG brand to me over mitsubishi. is LG air con good? the filter inside quality looks 'better' than the mitsubishi catechin filter .
From many user after were used LG before, they will said LG not as good cause after age got more noisy here & there.

But not sure for premium mirror model.
kimsim is offline  
Old 04-07-2015, 11:44 PM   #6060
Member
 
chomechome's Avatar
 
Join Date: Jan 2002
Posts: 475
Want to check for those big name like GC will they do site survey before commit? Saw today newspaper come with 5 years warranty but not sure whether it is for spare part or workmanship?
__________________
[SIZE=1]Idiot Qiang[/SIZE]
chomechome is offline  
Closed Thread
Important Forum Advisory Note
This forum is moderated by volunteer moderators who will react only to members' feedback on posts. Moderators are not employees or representatives of HWZ. Forum members and moderators are responsible for their own posts.

Please refer to our Terms of Service for more information.


Thread Tools

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are On