Air conditioning - Any recommendations please?? - Part 2

Jacqueline.

Senior Member
Joined
Mar 10, 2009
Messages
1,175
Reaction score
1
living room (38 square meter) = 15,925 BTU
1 bed room = 12sq metre so is 7,233 BTU /rm
2 bed room = 16sq metre so is 8,924 BTU /rm



or get
MXY-4G38VA2 (Outdoor unit) is 7.4kw = 25249.8508 BTU <-- turn on 3 room AC will spit into 8,416.61 BTU /rm
MSXY-FN10VE (indoor unit) X 3
MSXY-FN18VE (indoor unit) X 1
thanks for the recommendation, my budget only $5K, so i guess this would be the best

Mitsubishi Starmex inverter sys.4 (5 ticks)
FP series (R32)
Model: MXY4H38VG/10/10/10/18VG @ $4658.
 

harky

Great Supremacy Member
Deluxe Member
Joined
Jan 20, 2002
Messages
50,625
Reaction score
566
thanks for the recommendation, my budget only $5K, so i guess this would be the best

Mitsubishi Starmex inverter sys.4 (5 ticks)
FP series (R32)
Model: MXY4H38VG/10/10/10/18VG @ $4658.
cant find MXY4H38VG sia....
 

pandemonium147

Junior Member
Joined
Sep 6, 2002
Messages
9
Reaction score
0
The weight of MKM85VVGM (25.2k BTU) - Daikin ismile eco series is 52 kg and RKS71LVMG (24.2k BTU) - single split series is 71 kg. That will be a total of 123 kg.

Even with RKM71PVMG (24.2k BTU) - Smart envi series which is 60 kg, the total weight will be 112 kg with the ismile eco series, stil exceeding 110 kg.

I just read that no HDB approved permit is required to install 2 or less condensing units if their combined weight is less than, or equal to 110 kg.

Is this true for installation of 2 aircon systems?
If yes, is it easily obtainable with the new HDB concrete aircon ledge design?

Having 2 compressor systems also means that another aircon power plug will be needed, which also require HDB permit to install in the flat only has one.

I shouldn't need to worry about this since my hdb is new (under construction), right? hahaha ๐Ÿ˜…๐Ÿ˜…๐Ÿ˜…๐Ÿ˜…
 

batniss

Arch-Supremacy Member
Joined
Nov 23, 2015
Messages
15,702
Reaction score
259
The weight of MKM85VVGM (25.2k BTU) - Daikin ismile eco series is 52 kg and RKS71LVMG (24.2k BTU) - single split series is 71 kg. That will be a total of 123 kg.

Even with RKM71PVMG (24.2k BTU) - Smart envi series which is 60 kg, the total weight will be 112 kg with the ismile eco series, stil exceeding 110 kg.

I just read that no HDB approved permit is required to install 2 or less condensing units if their combined weight is less than, or equal to 110 kg.

Is this true for installation of 2 aircon systems?
If yes, is it easily obtainable with the new HDB concrete aircon ledge design?

Having 2 compressor systems also means that another aircon power plug will be needed, which also require HDB permit to install in the flat only has one.

I shouldn't need to worry about this since my hdb is new (under construction), right? hahaha ๐Ÿ˜…๐Ÿ˜…๐Ÿ˜…๐Ÿ˜…
yes to all.
 

GBC

Arch-Supremacy Member
Joined
Jan 1, 2000
Messages
17,410
Reaction score
625
The weight of MKM85VVGM (25.2k BTU) - Daikin ismile eco series is 52 kg and RKS71LVMG (24.2k BTU) - single split series is 71 kg. That will be a total of 123 kg.

Even with RKM71PVMG (24.2k BTU) - Smart envi series which is 60 kg, the total weight will be 112 kg with the ismile eco series, stil exceeding 110 kg.

I just read that no HDB approved permit is required to install 2 or less condensing units if their combined weight is less than, or equal to 110 kg.

Is this true for installation of 2 aircon systems?
If yes, is it easily obtainable with the new HDB concrete aircon ledge design?

Having 2 compressor systems also means that another aircon power plug will be needed, which also require HDB permit to install in the flat only has one.

I shouldn't need to worry about this since my hdb is new (under construction), right? hahaha ๐Ÿ˜…๐Ÿ˜…๐Ÿ˜…๐Ÿ˜…
Living & Dinning Room (5775 x 5625 + 3900 x 2825 = 43.5 sqm) at 16,825 cal. BTU
Your living and dinning room only require 16,825 BTU, so a RKS60LVMG (20,500 BTU) at 46 kg weight should be sufficient. So if you add 52 kg for MKM85VVGM (25.2k BTU) + 46 kg, its only 98 kg in total.
 

aErOpLaNe911

Senior Member
Joined
Sep 24, 2005
Messages
583
Reaction score
25
Waiting for 24k BTU indoor unit. Was told that have to wait until November, because of supply issues in Thailand.

Anyone facing the same issue?
 

pandemonium147

Junior Member
Joined
Sep 6, 2002
Messages
9
Reaction score
0
Living & Dinning Room (5775 x 5625 + 3900 x 2825 = 43.5 sqm) at 16,825 cal. BTU
Your living and dinning room only require 16,825 BTU, so a RKS60LVMG (20,500 BTU) at 46 kg weight should be sufficient. So if you add 52 kg for MKM85VVGM (25.2k BTU) + 46 kg, its only 98 kg in total.

Ah thanks, forgot to consider 22K aircon & compressor.. say go ask for quotes for all the different combinations.
Thank you all gurus for your advices!
 

joystick

Senior Member
Joined
Feb 7, 2001
Messages
599
Reaction score
0
Great thread. Read the last few pages and learn alot.

Old HDB 5RM. Looking at Daikin iSmileEco MKM75VVMG + 3x CTKM25VVMG (only turn on 2 units max)

Any reliable shop to recomment? Need to dispose of the current system as well.

TQ very much. Cheers.
 

agent_719

Master Member
Joined
Oct 6, 2011
Messages
3,384
Reaction score
354
If you want more cooling capacity, the only option is to top-up to the 4G38VA2 / 5G48VA2 condenser.

Performance for 4G33VA2:
LR only: 17K BTU
LR + 1BR: 13.5K + 7.6K
LR + 2BR: 9.9K + 5.5K per BR
LR + 3BR: 7.8K + 4.4K per BR

Performance for 4G38VA2:
LR only: 17K BTU
LR + 1BR: 15.3K + 9.5K
LR + 2BR: 11.2k + 6.3K per BR
LR + 3BR: 8.9K + 4.9K per BR

Your other alternative is to opt for 2 condenser setup, 1x sys1 (GN24VA) + 1x sys3 (3G28VA2):
LR only: 22.5K BTU
LR + 1BR: 22.5K + 9.5K
LR + 2BR: 22.5K + 9.5K per BR
LR + 3BR: 22.5K + 6.4K per BR

This 2 condenser setup is similar to my own home, where I have a single split for LR, and a sys3 for 3 BRs, of which only 2 BRs are used daily
Thank you so much for explanation.
My parents looking at 4G33VA2 with 1x 12k BTU 3x 9k BTU which was promoted by the salesman .

seems like we need to look at 4G38VA2.
Home is 4 bedroom kind so all 4 units will be for rooms
 

Ark Law

Arch-Supremacy Member
Joined
Jan 29, 2013
Messages
11,194
Reaction score
250
Thank you so much for explanation.
My parents looking at 4G33VA2 with 1x 12k BTU 3x 9k BTU which was promoted by the salesman .

seems like we need to look at 4G38VA2.
Home is 4 bedroom kind so all 4 units will be for rooms
Of course salesman will push and quote that the 4G33 is enough because the condenser will "push to max BTU" during the cooling phase. That ties in to the 4G33 being much cheaper to the 4G38, which will add to the likelihood of closing the sale with the customer.

Very unlikely any of them will show you the breakdown for your specific setup based on rated cooling capacity - where bold indicates FCU operating at rated capacity;

4G33VA2 w/ 1x FN13, 3x FN10 performance:
BR only: 9.5K
MBR only: 11.9K
BR + BR: 9.5K + 9.5K
MBR + BR: 11.1K + 8.9K
BR + BR + BR: 7.0K + 7.0K + 7.0K
MBR + BR + BR: 8.1K + 6.5K + 6.5K
MBR + BR + BR + BR: 6.2K + 4.9K + 4.9K + 4.9K

4G38VA2 w/ 1x FN13, 3x FN10 performance:
BR only: 9.5K
MBR only: 11.9K
BR + BR: 9.5K + 9.5K
MBR + BR: 11.9K + 9.5K
BR + BR + BR: 7.9K + 7.9K + 7.9K
MBR + BR + BR: 9.1K + 7.3K + 7.3K
MBR + BR + BR + BR: 7.0K + 5.6K + 5.6K + 5.6K

And what no online media will tell you is that Starmex's 5-tick range is essentially the old 2-tick range being given a handicap in order to achieve said efficiency;

4A38VA w/ 1x GE13, 3x GE10 performance:
BR only: 8.5K
MBR only: 11.9K
BR + BR: 8.5K + 8.5K
MBR + BR: 11.9K + 8.5K
BR + BR + BR: 8.5K + 8.5K + 8.5K
MBR + BR + BR: 11.9K + 8.5K +8.5K
MBR + BR + BR + BR: 9.9K + 7.1K + 7.1K + 7.1K
 

agent_719

Master Member
Joined
Oct 6, 2011
Messages
3,384
Reaction score
354
Of course salesman will push and quote that the 4G33 is enough because the condenser will "push to max BTU" during the cooling phase. That ties in to the 4G33 being much cheaper to the 4G38, which will add to the likelihood of closing the sale with the customer.

Very unlikely any of them will show you the breakdown for your specific setup based on rated cooling capacity - where bold indicates FCU operating at rated capacity;

4G33VA2 w/ 1x FN13, 3x FN10 performance:
BR only: 9.5K
MBR only: 11.9K
BR + BR: 9.5K + 9.5K
MBR + BR: 11.1K + 8.9K
BR + BR + BR: 7.0K + 7.0K + 7.0K
MBR + BR + BR: 8.1K + 6.5K + 6.5K
MBR + BR + BR + BR: 6.2K + 4.9K + 4.9K + 4.9K

4G38VA2 w/ 1x FN13, 3x FN10 performance:
BR only: 9.5K
MBR only: 11.9K
BR + BR: 9.5K + 9.5K
MBR + BR: 11.9K + 9.5K
BR + BR + BR: 7.9K + 7.9K + 7.9K
MBR + BR + BR: 9.1K + 7.3K + 7.3K
MBR + BR + BR + BR: 7.0K + 5.6K + 5.6K + 5.6K

And what no online media will tell you is that Starmex's 5-tick range is essentially the old 2-tick range being given a handicap in order to achieve said efficiency;

4A38VA w/ 1x GE13, 3x GE10 performance:
BR only: 8.5K
MBR only: 11.9K
BR + BR: 8.5K + 8.5K
MBR + BR: 11.9K + 8.5K
BR + BR + BR: 8.5K + 8.5K + 8.5K
MBR + BR + BR: 11.9K + 8.5K +8.5K
MBR + BR + BR + BR: 9.9K + 7.1K + 7.1K + 7.1K
So boss which brand/model will you recommend? Mitsubishi or Starmax ?
Our budget 5k+/- .
 

Ark Law

Arch-Supremacy Member
Joined
Jan 29, 2013
Messages
11,194
Reaction score
250
So boss which brand/model will you recommend? Mitsubishi or Starmax ?
Our budget 5k+/- .
Mitsubishi Electric is Starmex. Unless you're referring to Mitsubishi Heavy Industries, which is totally different.

Only reason I am biased to ME over Daikin is because ME is a lot more serviceable than Daikin's units.
 
Joined
Apr 19, 2018
Messages
203
Reaction score
4
Of course salesman will push and quote that the 4G33 is enough because the condenser will "push to max BTU" during the cooling phase. That ties in to the 4G33 being much cheaper to the 4G38, which will add to the likelihood of closing the sale with the customer.

Very unlikely any of them will show you the breakdown for your specific setup based on rated cooling capacity - where bold indicates FCU operating at rated capacity;

4G33VA2 w/ 1x FN13, 3x FN10 performance:
BR only: 9.5K
MBR only: 11.9K
BR + BR: 9.5K + 9.5K
MBR + BR: 11.1K + 8.9K
BR + BR + BR: 7.0K + 7.0K + 7.0K
MBR + BR + BR: 8.1K + 6.5K + 6.5K
MBR + BR + BR + BR: 6.2K + 4.9K + 4.9K + 4.9K

4G38VA2 w/ 1x FN13, 3x FN10 performance:
BR only: 9.5K
MBR only: 11.9K
BR + BR: 9.5K + 9.5K
MBR + BR: 11.9K + 9.5K
BR + BR + BR: 7.9K + 7.9K + 7.9K
MBR + BR + BR: 9.1K + 7.3K + 7.3K
MBR + BR + BR + BR: 7.0K + 5.6K + 5.6K + 5.6K

And what no online media will tell you is that Starmex's 5-tick range is essentially the old 2-tick range being given a handicap in order to achieve said efficiency;

4A38VA w/ 1x GE13, 3x GE10 performance:
BR only: 8.5K
MBR only: 11.9K
BR + BR: 8.5K + 8.5K
MBR + BR: 11.9K + 8.5K
BR + BR + BR: 8.5K + 8.5K + 8.5K
MBR + BR + BR: 11.9K + 8.5K +8.5K
MBR + BR + BR + BR: 9.9K + 7.1K + 7.1K + 7.1K
May I know how do you calculate the reduced cooling capacity?

Is there a factor? I'm trying to decide which system is more suitable for me.

Previously you gave suggestion for me:
Yep. Prices based on GC:
4G38VA2 (sys3) + GN18VA - $6240
3G28VA2 (sys3) + GN18VA - $5430
3G28VA2 (sys3) + GN24VA - $5670
4G33VA2 (sys4) - $4380
4G38VA2 (sys4) - $4960

Though you could scout other aircon contractors. I remember mine quoting me $1.8k for GN24
I'm still considering if I should top up extra $1k to get a separate system for living room. Have to discuss about the usage with my SO.
 

Ark Law

Arch-Supremacy Member
Joined
Jan 29, 2013
Messages
11,194
Reaction score
250
May I know how do you calculate the reduced cooling capacity?

Refer to manufacturer's spec sheet.

Current 5-sticks FN series:
CAhY72b.png

shdkFz7.png

IcnyVuj.png

uJEktuZ.png

Download: https://www.mitsubishielectric.com....bishi_Starmex_Catalogue_Book_Jun20.ashx?la=en

Discontinued 2-ticks GE series:
 

GBC

Arch-Supremacy Member
Joined
Jan 1, 2000
Messages
17,410
Reaction score
625
May I know how do you calculate the reduced cooling capacity?

Is there a factor? I'm trying to decide which system is more suitable for me.

Previously you gave suggestion for me:

I'm still considering if I should top up extra $1k to get a separate system for living room. Have to discuss about the usage with my SO.
You need to think carefully.. Buy an underpowered system and it's going to stay with you for the next 7 years + and it will effect the enjoyment of your aircon system.

Trying to rectify an underpower aircon system after that is not going to be $1k either. so don't be a case of penny wise pound foolish.
 

petetherock

Moderator
Moderator
Joined
Jan 7, 2007
Messages
8,298
Reaction score
147
You need to think carefully.. Buy an underpowered system and it's going to stay with you for the next 7 years + and it will effect the enjoyment of your aircon system.

Trying to rectify an underpower aircon system after that is not going to be $1k either. so don't be a case of penny wise pound foolish.
You see the trend here
People asking these questions donโ€™t read past entries and always ask if a smaller and cheaper compressor will suffice โ€ฆ
 
Joined
Apr 19, 2018
Messages
203
Reaction score
4
Just went to gain city, nearly bought the system4 with 4G33VA2 at $4k.

After much considerations, I think I will go with 3G28 + 3xFN10 and GN24 for living room.

Total costs around $4.8k from letscoolaircon.com.

Only downside is the CU not enough to power all 3 bedrooms at the same time.
 

Elloell

Senior Member
Joined
Dec 29, 2009
Messages
1,647
Reaction score
0
Hello Gurus, need some help here .
Am renovating a 4 room BTO and got a system 4 package of MKM85VVMG compressor + 24/12/9/9k

originally paid deposit for daikon eco iSmile series (R32), been told itโ€™s oos for now . The salesperson suggested to me swap to daikin iSmile series or Mitsubishi Starmex R32 . Should I wait for stock to arrive or swap to starmex since itโ€™s R32 system too .

Mitsubishi starmex bundle is MXY4H33VG and 24/12/9/9 (R32 gas)
Thanks in advance
 
Last edited:

GBC

Arch-Supremacy Member
Joined
Jan 1, 2000
Messages
17,410
Reaction score
625
Hello Gurus, need some help here .
Am renovating a 4 room BTO and got a system 4 package of MKM85VVMG compressor + 24/12/9/9k

originally paid deposit for daikon eco iSmile series (R32), been told itโ€™s oos for now . The salesperson suggested to me swap to daikin iSmile series or Mitsubishi Starmex R32 . Should I wait for stock to arrive or swap to starmex since itโ€™s R32 system too .

Mitsubishi starmex bundle is MXY4H33VG and 24/12/9/9 (R32 gas)
Thanks in advance
You should first re-look at your aircon confguration, it's way underpowered...
How can a MKM85VVMG compressor (25K BTU) support 4 indoor units ie 24k+12K+9K+9K = 54k BTU in total.
 