Hi terumo;
ME Tech came by to check. They did 2 kind of check, one for the outdoor and one for the indoor. The check was done focusing only on the Main bdrm as that was what I complaint about that was not cool enough. The AC was allow to run for a while (abt 15-20mins before they start doing the check). They also set the Main bdrm FCU to 16 deg C and FULL fan speed (ie 4-bars=maximum)
Outdoor:
1. They check the compressor (think that's what they call it) and said that the reading was stable (one of the equipment used was a ring-like meter with numbers shown on the display). They mentioned that the current drawn was within the ME spec. Hence, they concluded to be ok.
2. They check the gas with some kind of gauges and was ok, no overcharge or undercharge.
3. Ask them about the cross or bent pipe, ME Tech advise that since there is no fluctuation from the measurement, it can be concluded that there is no cross or bent pipe.
Indoor FCU:
1. The ME Tech use some kind of equipment to measure the "cold-air" coming out from the the FCU. The equipment was place very near to the running fan. Was shown the reading abt 14 deg C. Was told the technical spec for the FCU was in the range of 10-15 deg C. The reading "improve" to abt 11.7 deg C after about 1 1/2 hours. Based on this, they concluded that the FCU and the sensor to be ok. I was told that there was an opening on the side of the FCU for the temp sensor and that the opening should not be block for proper function of the FCU.
2. ME Tech concluded that as the FCU in the Main bdrm is giving the "cold" air according to the remote control input, there is no cross wire or cross pipe connection.
However, the Main bdrm temperature was able to come down to abt 21 deg C using the "equipment" that I'd previously been using to measure the other bdrms. The only difference now is that the "equipment" was place facing the FCU (abt 3.5 meter away and in front of the FCU) as compared to the previous occassion of placing it directly below under the FCU, about 1.5 meters below. They then set the remote control temperature back to 18 deg C and the room temp is able to maintain at 21 deg C.
So, since that the equipment & FCU are found to be ok and within the ME tech spec, there is really nothing they can do or fix. At least, there is no cross pipe and no cross wire, and no gas shortage and no bent pipe issue. So, no installer issue.
Now thinking back, I should have requested that they check the Main bdrm with all 3 FCUs running and see if able to achieve the 21-23 deg C for all the 3 bdrms that I was wishing for.
But at least now, in order to achieve the room temperature that I want, my understanding is that I need to
run the fan at maximum speed+lowest temperature setting until the require room temperature is achieved and then
reduce the fan speed and increase the temperature to the required temperature for the FCU to maintain.
So, in my conclusion, the possibility of "under-size" on the FCU for the Main bdrm keeps ringing in my mind. But,
if you have any views or input or advise, do share with me. Thanks in advance.
Did ask for the ME Tech advise/input on the size of the FCU for the Main bdrm, based on my requirement of running all the 3 FCUs together and to achieve a room temperature of 21 deg C. In their own opinion (not ME) and purely on tech spec, the 18k FCU is prefer over the 24k FCU. This is because the 24k FCU may affect the 2 other smaller bdrm when all the 3 FCUs are running, while with the 18k FCU, will have the "ideal loading", ie the outdoor match with that of the indoors requirement. This will also save the haste from future complain that the other rooms may not be cool enough.
Any comments?
Also, they rather I check with AC installer with better knowledge on sizing of the Room to FCU requirement.
Meanwhile, will continue to monitor over the next few days and see if I can "re-adapt" and adjust to this "new" expectation of the FCU, or any new discovery.
To ulupandan,
Call ME and see what they comment.
They should be able to find cause of fault, if piping is @ fault, your installer have to come back and settle it. Not ME.
ME only warranty the equipment.
Gas level should be ok, as the other 2 rooms is cold (IMO)