Hi bro dachee,

Based on 3 friends and relatives, keep tell me starmex cannot go wrong one. That's why I am here reading see if can get a recommended model for system 4 or to get a 3 +1

Hi, StarMex has a 4 ticks single split system, 2 ticks and 5 ticks for other configurations.

They are different in some ways though they are all StarMex. The reliability of air conditioner depends on both the product as well as the installation. Good product can fail if installation is poorly done.

From the specs, features as well as the support, this product can be considered. Again, you need to check your configuration.

Hope above is helpful.
 

orangeman

Master Member
Joined
Jul 5, 2010
Messages
4,191
Reaction score
3
Hi, StarMex has a 4 ticks single split system, 2 ticks and 5 ticks for other configurations.

They are different in some ways though they are all StarMex. The reliability of air conditioner depends on both the product as well as the installation. Good product can fail if installation is poorly done.

From the specs, features as well as the support, this product can be considered. Again, you need to check your configuration.

Hope above is helpful.

Ok, my config now is down to 2 options.
1) system 4 starmex, living room BTU 12000 ....other 3 9000 (not sure if can change living room to 18000)
2) system 3 12000-9000-9000, system 1 one FCU....
Read though the pages here, seems to be go for the 2 ticks for reliability
 

dachee

Member
Joined
Nov 18, 2016
Messages
262
Reaction score
1
Ok, my config now is down to 2 options.
1) system 4 starmex, living room BTU 12000 ....other 3 9000 (not sure if can change living room to 18000)
2) system 3 12000-9000-9000, system 1 one FCU....
Read though the pages here, seems to be go for the 2 ticks for reliability

To other readers, Any comments from you? Do share your experiences.
 

dachee

Member
Joined
Nov 18, 2016
Messages
262
Reaction score
1
Ok, my config now is down to 2 options.
1) system 4 starmex, living room BTU 12000 ....other 3 9000 (not sure if can change living room to 18000)
2) system 3 12000-9000-9000, system 1 one FCU....
Read though the pages here, seems to be go for the 2 ticks for reliability

Hi,

1. System 4 SatrMex can have the following combination for HDB with limited current (assuming that you are in HDB with limited current, do let me know if I am wrong) There are HDB without limited current too.

For the condenser MXY-4A28VA (2 ticks) with total indoor capacity not exceeding 15.6kW or 53,229 Btu, you can have FCUs combination of 10+10+10=13/18/24/26. So having 18 kW for the living room is possible.

However with this condenser, each FCUs will only have the following max. capacity and not the individual FCU max capacity.

10+10+10+13 = 1.8 kW (6.1k Btu); 1.8; 1.8; 1.8 kW (6.1k Btu) = total 7.2 OR
10+10+10+18 = 1.5 kW (5.1k Btu); 1.5; 1.5; 2.7 kW (9.2k Btu)= total 7.2

According to the spec, the FCU "10" has a capacity of 2.5 kW (8.5k Btu) but in this system 4 configuration all the FCUs are under utilized. And your FCU "13" is now running lesser than the FCU "10" of 2.5 kW.

When you increase your system 4 combination to include FCU "18", your FCU "10" drop to 1.5 kW (5.1k Btu).

So you need to be careful in selecting the configuration.

Alternatively you can up size your system 4 to a 38VA which will give you the following:

10+10+10+13 = 1.82; 1.82; 1.82; 2.54 = 8.0 kW OR
10+10+10+18 = 1.60; 1.60; 1.60; 3.20 = 8.0 kW

Noticed that all FCUs are not running at full capacity. The FCU 13 and 18 can run at full capacity of 3.5 kW (11.9k Btu) and 5 kW (17k Btu).

2. The System 3 +1 combination seems to give better capacity for each FCU when compare to system 4.

But you may wish to check the installation and combination prices of 13+10+10 and 10 as well as 10+10+10 and 13. Check the FCU capacity for each combination. They are quite close.

The above are my opinion and hope that they are helpful.
 

terumo

Senior Member
Joined
Oct 20, 2004
Messages
1,908
Reaction score
1
To miketan_wh,

If system 1 x 2, you have to factor additional power point & bracket too, which adds up to be higher in some cases.
 

dachee

Member
Joined
Nov 18, 2016
Messages
262
Reaction score
1
To miketan_wh,

If system 1 x 2, you have to factor additional power point & bracket too, which adds up to be higher in some cases.

Terumo is right. Each condenser would needs its own power point at the condenser and breaker at the DB. Bracket is subject to its need.

For other reader who may have sufficient space to install 2 condensers, you may wish to consider your usage pattern. If you use 1 FCU most of the time and another FCU rarely, then in the event that the frequently used condenser is down and need replacement, the other system will still be operational and relatively new. However if you have a system 2, then both FCUs will be affected and the replacement of a system 2 condenser will be more expensive.

Good to do your maths not only for unit and installation cost but also operational and maintenance cost.

Above are my opinon, hope that they are helpful.
 
Last edited:

leobox1

Senior Member
Joined
Dec 24, 2007
Messages
1,357
Reaction score
2
Hi experts.. I am changing old star Mex ( 11 years ). As I on very cold still tough to cool down.

Mine is 4room

Unit is
Living room ( use once in blue moon )
MBR ( about 12 hours a day )
Br 1 ( about 8 hours a day )
Br 2 ( about 1 hour a day )

Hence I guess I need super energy saving ..

Means I must buy MXY-4G28VA ? This got 4 ticks. Thanks
 

dachee

Member
Joined
Nov 18, 2016
Messages
262
Reaction score
1
Hi experts.. I am changing old star Mex ( 11 years ). As I on very cold still tough to cool down.

Mine is 4room

Unit is
Living room ( use once in blue moon )
MBR ( about 12 hours a day )
Br 1 ( about 8 hours a day )
Br 2 ( about 1 hour a day )

Hence I guess I need super energy saving ..

Means I must buy MXY-4G28VA ? This got 4 ticks. Thanks

Hi,

May I know what temperatures are normally set for each respective rooms?

Pls clarify what you mean by: As I on very cold still tough to cool down.
 
Last edited:

leobox1

Senior Member
Joined
Dec 24, 2007
Messages
1,357
Reaction score
2
Ok .. Thanks.

As in now I have to set like 16 degrees high fan just to get the room to cool. Usually no.

I normally like to set 23 degree
 

orangeman

Master Member
Joined
Jul 5, 2010
Messages
4,191
Reaction score
3
Hi,

1. System 4 SatrMex can have the following combination for HDB with limited current (assuming that you are in HDB with limited current, do let me know if I am wrong) There are HDB without limited current too.

For the condenser MXY-4A28VA (2 ticks) with total indoor capacity not exceeding 15.6kW or 53,229 Btu, you can have FCUs combination of 10+10+10=13/18/24/26. So having 18 kW for the living room is possible.

However with this condenser, each FCUs will only have the following max. capacity and not the individual FCU max capacity.

10+10+10+13 = 1.8 kW (6.1k Btu); 1.8; 1.8; 1.8 kW (6.1k Btu) = total 7.2 OR
10+10+10+18 = 1.5 kW (5.1k Btu); 1.5; 1.5; 2.7 kW (9.2k Btu)= total 7.2

According to the spec, the FCU "10" has a capacity of 2.5 kW (8.5k Btu) but in this system 4 configuration all the FCUs are under utilized. And your FCU "13" is now running lesser than the FCU "10" of 2.5 kW.

When you increase your system 4 combination to include FCU "18", your FCU "10" drop to 1.5 kW (5.1k Btu).

So you need to be careful in selecting the configuration.

Alternatively you can up size your system 4 to a 38VA which will give you the following:

10+10+10+13 = 1.82; 1.82; 1.82; 2.54 = 8.0 kW OR
10+10+10+18 = 1.60; 1.60; 1.60; 3.20 = 8.0 kW

Noticed that all FCUs are not running at full capacity. The FCU 13 and 18 can run at full capacity of 3.5 kW (11.9k Btu) and 5 kW (17k Btu).

2. The System 3 +1 combination seems to give better capacity for each FCU when compare to system 4.

But you may wish to check the installation and combination prices of 13+10+10 and 10 as well as 10+10+10 and 13. Check the FCU capacity for each combination. They are quite close.

The above are my opinion and hope that they are helpful.

Hi bro dachee,
This is definitely very useful....thanks for clearing my doubts
 

dachee

Member
Joined
Nov 18, 2016
Messages
262
Reaction score
1
Air conditioner DIY group.

Hi, Is there anyone here who is interested to form a DIY group to provide installation of air conditioners for each other for free with the objective of keeping a high standard in the air conditioner installation as well as addressing the over charge cost and poor workmanship from the installation industry?

Members can also help each other in maintaining each other's air conditioners and trouble shoot if any. Arrangement will be made for members to attend appropriate courses.

For example, some times, an air conditioner is not cold because the compressor in the condenser does not kick in (start). This fault is likely due to a defective start capacitor that helps the compressor motor to start turning. A contractor would likely charge you $180-200 for checking and replacing the capacitor which takes about 10 mins work. The cost of a capacitor is less than $10. Doing this simple repair work yourself can save you lots of unnecessary money and sometime problem with contractor poor workmanship.

There is no sex restriction for members.

What do you all think about this? Will it work?
 

dachee

Member
Joined
Nov 18, 2016
Messages
262
Reaction score
1
Ok .. Thanks.

As in now I have to set like 16 degrees high fan just to get the room to cool. Usually no.

I normally like to set 23 degree

1. May I know what is your StarMex model (indoor and outdoor) that you are currently having?

2. Does this cooling problem happen only in some, all or only one room?

3. Did you have the problem checked and what is their diagnosis?

4. Or you just want to change because yours is already 11 year old?
 

leobox1

Senior Member
Joined
Dec 24, 2007
Messages
1,357
Reaction score
2
1. May I know what is your StarMex model (indoor and outdoor) that you are currently having?

2. Does this cooling problem happen only in some, all or only one room?

3. Did you have the problem checked and what is their diagnosis?

4. Or you just want to change because yours is already 11 year old?

I not sure the model :(

But it only happens with one unit .. The MBR one. Chemical wash also not much help :(
 

wqwqwq

Junior Member
Joined
Apr 22, 2012
Messages
13
Reaction score
0
So sorry to hear this, I was also being introduced to LG recently when I visited Gain City. But I had not made any purchase as my BTO was not ready at the time.

While trying to do some homework on air con, I was lucky to bump into an air con repair specialist who was working in my workplace the other day.

And I was warned to stay clear of certain brands and he himself was using Mitsubishi Starmex.

And please take note that Mitsubushi air con for residential home comes in "two brands". Mistubishi Electric (Starmex) & Mitsubushi Heavy Industry. So please take note when you are purchasing "Mitsubishi" air con.

Hope this helps for those who are looking at Mitsubishi air con currently.

Visited Gain City to buy Mitsubishi for my resale HDB 5 room house but was talked into buying LG System 3 insteadfrom Gain City.

Since we moved Into our fully renovated house beginning this year, we have so much headaches

1. Compressor dented and collected rain water - small matter and settled quickly.

2. Hot air blewing shortly after 2 months or so. Called Gain City and LG man came. Said gas leak and not product problem.

3. Gain City's sub contractor came, said need to do minor hacking to attach devices to detect where the gas leakage was. But I monitor first after he him tightened a knot in the compressor. Fortunately it worked.

4. First service done by Gain City also disappointing. The senior technician still ok but the junior simply talked too much, messy and untidy. But worst, was told one unit cannot be serviced as the trunking blocked the aircon and cover couldn't be removed. Need to relocate the unit.

5. Gain City's sub contractors came the next week. Either to relocate and move the unit upward or opened up the trunking every time servicing is done. I took the 2nd option to avoid all the messes and inconvenience.

6. The same unit started to make funny noise whenever I switched it on. On nights when I sleep light, I feel irritated by the noises.

7. Worst of all, rain water started to sip into master room lately!!! Given my feedback in Gain City 3 days ago, asking for a complete solution but no response from them yet!!!

I am considering to seek help from another aircon company and also give up my 2 year service contract with Gain City. Any recommendations?

If Gain City cannot resolve my problems once and for all, I hope another company can.
 

dachee

Member
Joined
Nov 18, 2016
Messages
262
Reaction score
1
MBR is msxy ga10va

Hi, if I am not wrong, the MSXY-GA10VA is paired with the MXY-4A28VA or 38VA if you have only one condenser outside. This condenser is 2 ticks and is still selling in the market.

Though this model is out for many years, it is relatively new (meaning people are still buying it as new model for this home).

Depending on the detail of the problem, you may have a FCU (the one in the MBR) issue or the piping issue rather than the whole system. Is your MBR FCU very near to your outside condenser? What is the estimated piping length between both of them? Around 2 - 3 meters?

It may not be worth changing the whole system.
 
Last edited:

leobox1

Senior Member
Joined
Dec 24, 2007
Messages
1,357
Reaction score
2
Hi, if I am not wrong, the MSXY-GA10VA is paired with the MXY-4A28VA or 38VA if you have only one condenser outside. This condenser is 2 ticks and is still selling in the market.

Though this model is out for many years, it is relatively new (meaning people are still buying it as new model for this home).

Depending on the detail of the problem, you may have a FCU (the one in the MBR) issue rather than the whole system. Is your MBR FCU very near to your outside condenser? What is the estimated piping length between both of them? Around 2 - 3 meters?

It may not be worth changing the whole system.

Yes .. Only one condenser.

I think should be short because just by the left is the Aircon ledge liao. But 2 ticks means I pay alot in electric right ? :(
 

dachee

Member
Joined
Nov 18, 2016
Messages
262
Reaction score
1
Yes .. Only one condenser.

I think should be short because just by the left is the Aircon ledge liao. But 2 ticks means I pay alot in electric right ? :(

Yes and no.

Though the FJ series with MXY-4G28VA has 5 ticks, its max capacity for a 10+10+10+10 configuration is only 6.5kW (22k Btu), while your existing MXY-4A28VA (with limiting current) has max capacity of 7.2kW (24.5k Btu).

It therefore depends on the temperature setting that you which to achieve for each room. From the spec, full capacity of each FCU cannot be achieved with either 4G or 4A condenser, even if you up-size to 38VA for the condenser.

By the way, the 5 ticks COP full load of 4.89 is just 0.03 above the NEA's rating of 4.86. So it is very close to only 4 ticks (high side).

You may wish to do an running cost vs initial cost to see what saving you are getting. It may be good to know that other users of the 5 ticks model is paying for their usage pattern.

The above are my opinion and hope that they are useful.
 
Status
Not open for further replies.
Important Forum Advisory Note
This forum is moderated by volunteer moderators who will react only to members' feedback on posts. Moderators are not employees or representatives of HWZ Forums. Forum members and moderators are responsible for their own posts. Please refer to our Community Guidelines and Standards and Terms and Conditions for more information.