Ok, my config now is down to 2 options.
1) system 4 starmex, living room BTU 12000 ....other 3 9000 (not sure if can change living room to 18000)
2) system 3 12000-9000-9000, system 1 one FCU....
Read though the pages here, seems to be go for the 2 ticks for reliability
Hi,
1. System 4 SatrMex can have the following combination for HDB with limited current (assuming that you are in HDB with limited current, do let me know if I am wrong) There are HDB without limited current too.
For the condenser MXY-4A28VA (2 ticks) with total indoor capacity not exceeding 15.6kW or 53,229 Btu, you can have FCUs combination of 10+10+10=13/18/24/26. So having 18 kW for the living room is possible.
However with this condenser, each FCUs will only have the following max. capacity and not the individual FCU max capacity.
10+10+10+13 = 1.8 kW (6.1k Btu); 1.8; 1.8; 1.8 kW (6.1k Btu) = total 7.2 OR
10+10+10+18 = 1.5 kW (5.1k Btu); 1.5; 1.5; 2.7 kW (9.2k Btu)= total 7.2
According to the spec, the FCU "10" has a capacity of 2.5 kW (8.5k Btu) but in this system 4 configuration all the FCUs are under utilized. And your FCU "13" is now running lesser than the FCU "10" of 2.5 kW.
When you increase your system 4 combination to include FCU "18", your FCU "10" drop to 1.5 kW (5.1k Btu).
So you need to be careful in selecting the configuration.
Alternatively you can up size your system 4 to a 38VA which will give you the following:
10+10+10+13 = 1.82; 1.82; 1.82; 2.54 = 8.0 kW OR
10+10+10+18 = 1.60; 1.60; 1.60; 3.20 = 8.0 kW
Noticed that all FCUs are not running at full capacity. The FCU 13 and 18 can run at full capacity of 3.5 kW (11.9k Btu) and 5 kW (17k Btu).
2. The System 3 +1 combination seems to give better capacity for each FCU when compare to system 4.
But you may wish to check the installation and combination prices of 13+10+10 and 10 as well as 10+10+10 and 13. Check the FCU capacity for each combination. They are quite close.
The above are my opinion and hope that they are helpful.