Daiken inverter.
I don't know the exact model, but I have 2 instructions manual.
1. FTKD25DVM, FTKD35DVM
2. FTKD50BVM, FTKD60BVM, FTKD71BVM
I don't know the btu of each. The 2 living room units are the wider blower while the other 2 blowers in each of the bedrooms are smaller.
The seller just told me if the existing is system 2 x 2, I cannot just change to system 4..
Ok now i found that, ur setting for existing copper pipe size for 50 = 2hp & 60 = 2.5hp with 70 = 3hp that copper size too large, maybe not be suitable for system 4.
Look like the best set up to be change all copper pipe and rerun with tracking only.
To be save to hack off and re-concealed wall.
For example on system 4.
10k & 13k same copper size for 9mm & 6mm only
18k for 12mm & 6mm
26k btu for gas 15mm dia & 9mm dia for liquid size.
But your existing set up on Daikin
25 for 9mm & 6mm
35 for 12mm & 6mm
50 for 15mm & 6mm
60 for 15mm & 9mm
70 for 15mm & 9mm
Over here was different between the size and not suitable for system 4.