Air conditioning - Any recommendations please??

Status
Not open for further replies.

dachee

Member
Joined
Nov 18, 2016
Messages
262
Reaction score
1
Ceiling height is 2.9M

Hi, taking that the total volume is 4X4X2.9 = 46.4m3 and that the exterior temperature is 32 degree and you would like to achieve a 20 degree interior temperature, ie a decrease of 12 degree, you would need a system to provide a FCU capacity of 5.8k btu or 1.7kW at normal insulation for this room. This is only theoretical. Higher capacity may be required if there are other heat source/s within the bedrooms or living room and other openings that allow hot air to get into the room/s.

You may notice that unlike a single split and some system 2 that provide the same indoor and outdoor capacity, system 3 and 4 do not provide the total capacity of all indoor FCUs when all FCUs are used with temperature setting that requires more than the nominal rating.

The above are my opinion and hope that they are useful.
 

dachee

Member
Joined
Nov 18, 2016
Messages
262
Reaction score
1
Guys, I am a noob to aircon.

I have set the fan speed to AUTO and mode to COOL.

Is it normal when I first turn on the air con, the fan takes sometime to startup?

Its not like instant the fan starts running. However once I switch it to HIGH/MEDIUM, it adjusts automatically

Hi, it would be good if you can clarify the fan you are referring to. Is it the indoor (FCU) fan or the outdoor (condenser) fan?

What do you mean that "it adjusts automatically"?
 

gardiboy

Master Member
Joined
May 25, 2004
Messages
2,738
Reaction score
1
Hi, it would be good if you can clarify the fan you are referring to. Is it the indoor (FCU) fan or the outdoor (condenser) fan?

What do you mean that "it adjusts automatically"?

I can referring to the FCU.

Means, when I turn 'on' the aircon, and if fan mode is set to 'auto', the fcu takes about 1-2 mins to detect and turn up the fan speed. is this normal?

However, I can directly bring the fan speed up to high to avoid the 1-2mins wait.
 

dachee

Member
Joined
Nov 18, 2016
Messages
262
Reaction score
1
I can referring to the FCU.

Means, when I turn 'on' the aircon, and if fan mode is set to 'auto', the fcu takes about 1-2 mins to detect and turn up the fan speed. is this normal?

However, I can directly bring the fan speed up to high to avoid the 1-2mins wait.

Hi, Personally, I don't think this is normal, especially from a user's point of view. However, it may be some software development issue and it will be good to call the technical support for your air conditioner brand to check with them.

It may also be good if you can provide the brand and model so that other readers who are using it can provide their comments.
 

dachee

Member
Joined
Nov 18, 2016
Messages
262
Reaction score
1
Saw a Facebook post on Panasonic sky series. Seems that this will be released in Singapore soon.

Here's the link from Panasonic Malaysia website -> http://airconditioner.my.panasonic.com/sky-series

Thanks. Good infor. Noticed that in the ad. it was mentioned that the air is blown up towards the ceiling to cool the room. This brings me to the topic of wall mounted FCU placement height.

If you have a high ceiling room, is placing the wall mounted FCU near the ceiling the right place, or is there a specific height that the FCU should be placed?

How about the placement of the wall mounted FCU relative to the condenser? Is there some relationship between them?

What do you think? Please provide your comments/understanding or even those advises given by your contractors / installers, or your decision as to why you have installed your wall mounted FCU at its current location.
 
Last edited:

yamashita

Moderator
Moderator
Joined
Dec 23, 2000
Messages
9,676
Reaction score
51
Thanks. Good infor. Noticed that in the ad. it was mentioned that the air is blown up towards the ceiling to cool the room. This brings me to the topic of wall mounted FCU placement height.

If you have a high ceiling room, is placing the wall mounted FCU near the ceiling the right place, or is there a specific height that the FCU should be placed?

How about the placement of the wall mounted FCU relative to the condenser? Is there some relationship between them?

What do you think? Please provide your comments/understanding or even those advises given by your contractors / installers, or your decision as to why you have installed your wall mounted FCU at its current location.

I have decided on Panasonic CU-XS9RKZ but it's current out of stock for my installer. Don't think I will change my decision as I doubt the sky series will be introduced to Singapore by year end.

The cooling method of sky series seems to make sense. It is unclear on the energy consumption for having 2 cooling outlets (downward and upward) as compared to the conventional downward outlet.

Another doubt I have is condensation resulting from temperature differential of my false ceiling and the upward cooling outlet. Above my false ceiling is the house roof and in hot weather, the differential may cause dampness.
 

dachee

Member
Joined
Nov 18, 2016
Messages
262
Reaction score
1
I have decided on Panasonic CU-XS9RKZ but it's current out of stock for my installer. Don't think I will change my decision as I doubt the sky series will be introduced to Singapore by year end.

The cooling method of sky series seems to make sense. It is unclear on the energy consumption for having 2 cooling outlets (downward and upward) as compared to the conventional downward outlet.

Another doubt I have is condensation resulting from temperature differential of my false ceiling and the upward cooling outlet. Above my false ceiling is the house roof and in hot weather, the differential may cause dampness.

It will be good if other readers can provide their comments too.
 

terumo

Senior Member
Joined
Oct 20, 2004
Messages
1,908
Reaction score
1
To yamashita,

The dual cooling outlets will have little effect on the energy consumption. (IMO)

By the way, i think Sky Series is already launched in SG.
 
Last edited:

orangeman

Master Member
Joined
Jul 5, 2010
Messages
4,191
Reaction score
3
Hi, taking that the total volume is 4X4X2.9 = 46.4m3 and that the exterior temperature is 32 degree and you would like to achieve a 20 degree interior temperature, ie a decrease of 12 degree, you would need a system to provide a FCU capacity of 5.8k btu or 1.7kW at normal insulation for this room. This is only theoretical. Higher capacity may be required if there are other heat source/s within the bedrooms or living room and other openings that allow hot air to get into the room/s.

You may notice that unlike a single split and some system 2 that provide the same indoor and outdoor capacity, system 3 and 4 do not provide the total capacity of all indoor FCUs when all FCUs are used with temperature setting that requires more than the nominal rating.

The above are my opinion and hope that they are useful.

Thanks for the detailed explanation... So if I take it from a newbie point of view I don't really need a 18k fcu for my living room If most of the time I only on 2 fcu right? 12k should be ok and additional 3 9k each...?
 

yamashita

Moderator
Moderator
Joined
Dec 23, 2000
Messages
9,676
Reaction score
51
To yamashita,

The dual cooling outlets will have little effect on the energy consumption. (IMO)

By the way, i think Sky Series is already launched in SG.

Thanks! I didnt find this model on Panasonic Singapore website, I assumed it has not been launched yet.

Just messaged my installer, waiting for her to come back with the details. :)
 

yamashita

Moderator
Moderator
Joined
Dec 23, 2000
Messages
9,676
Reaction score
51
To yamashita,

The dual cooling outlets will have little effect on the energy consumption. (IMO)

By the way, i think Sky Series is already launched in SG.

Correction to my earlier post, just watched the product video for sky series. There is only 1 cooling outlet.

 

dachee

Member
Joined
Nov 18, 2016
Messages
262
Reaction score
1
Thanks for the detailed explanation... So if I take it from a newbie point of view I don't really need a 18k fcu for my living room If most of the time I only on 2 fcu right? 12k should be ok and additional 3 9k each...?

Hi, did a back search but cannot find you mentioning the brand and model of the system 4 that you intend to buy. This is because, different models have different configuration constrains. It is good if you can provide them.
 

dachee

Member
Joined
Nov 18, 2016
Messages
262
Reaction score
1
Correction to my earlier post, just watched the product video for sky series. There is only 1 cooling outlet.


Hi, personally, I cannot agree with the advertisement concept of cooling the ceiling in order to cool the room effectively. I feel that the basic objective for installing an air conditioner is forgotten, which in my opinion should be to provide a comfortable environment to the occupants and not to cool the room.

Depending on the climate in a country, the FCU is located at a height that effectively provides comfort to the occupants. In many citing and is also my opinion that the FCU should be location at a height of 8 ft plus or minus, from the floor. Unnecessary cooling can result in higher energy usage.

Cool air is heavier than warm air and therefore, cool air will sink towards the floor while warm air will raise towards the ceiling. It is not advantages to mixed them and therefore these 2 sections of air is left alone so that the cool air section keep the occupants comfortable while the warm air section stays at the top away from the occupants and use no energy. The layer of air in between the cool and warm air is the layer that the FCU draws into it to cool. So the location of the FCU determines this layer and ultimately the comfort of the occupants.

There are also other considerations in regards to the placement of the FCU. Would anyone wish to share their though?

Above are my opinion and hope that they are useful.
 

rubber33

Master Member
Joined
Apr 8, 2005
Messages
2,719
Reaction score
146
Copy and paste from a fb ad.

Dear Fans!

We just missed Black Friday by a few minutes!
But our Panasonic Sky Series Black Friday sale will still go on!
Beat the Queue, we will come to you!

Introducing Panasonic Latest "Radiant Cooling" Technology, this will change the way an air conditioner cools down your room.
- Solve the issue of "Cold Air" blowing directly at you the whole night.
- Cools the room down Gently and Evenly.
- Helps to maintain Skin Moisture and Eliminates the "Dry" feeling.

Along with its Excellent Air Purifier capable of purifying up to PM 2.5 Dust Particles.
- Dust Sensor automatically activates when room has high level of dust concentration.
- Rest and Sleep in Clean and Fresh environment.

With its New P-TECh Inverter Technology which allows it to achieve maximum frequency in the shortest period of time.
- Rated 3 ticks energy efficiency by NEA which cost only 50 cents for a room usage per night (based on 8 hours)

Panasonic Sky Series
- Where Comfort, Health and Beauty combine into One.

To learn more about Tomorrow Technology Today, just comment "Email me" or leave your contact details at

Link >> https://goo.gl/cqwTBx

We will email you a Free E Book explaining more about its Features and the Benefits that it will bring to you and your family.
We will also give you another E Book giving you the Energy Consumption of the various brands as BONUS.

Plus, we will come down to your home for a Free Site Survey to explain on the installation process and the system that we use.

Limited Sets Available Only for Black Friday Pre-Launch Sale!
Normal price $3980.
Black Friday Sale Price $3680.
First 5 sets with Free Upgrade to 12k Btu for master room worth $150!
Be among the FIRST Few in Singapore to Own One!

By the way, we are giving 5 Lucky Fans that download the E Book one set of Panasonic Veggie Life Salad each!

Promo ends 15th December!

Download the E Book today at

Link>> https://goo.gl/cqwTBx

#PanasonicSG #PanasonicVeggieLife
 

rubber33

Master Member
Joined
Apr 8, 2005
Messages
2,719
Reaction score
146
Was thinking to get star mex.. But now with this panasonic, probably wait and see.. Since have air purifier which will be good during hazy period..
 

darkfuryex

Senior Member
Joined
Mar 20, 2007
Messages
1,552
Reaction score
3
hi bros...anyone got contact for reliable aircon installation service + cleaning services ?

does the uncle auntie or ah yi does installation service?

thanks bros!!
 

bonkbonk

Supremacy Member
Joined
Mar 17, 2001
Messages
7,003
Reaction score
5
anyone on europace aircon ?

they claim using Mitsubishi engine/motor not sure of it... is it reliable ?
 

carlos83

Junior Member
Joined
May 23, 2009
Messages
17
Reaction score
0
Hello.

I am thinking of getting aircon for my 5rm flat and would need some help here.
Currently only 2 of us and aircon will only be used in MBR during hot weather or haze. Usually we sleep with just fan and windows open.

Wonder if I need inverter model or non inverter model will be good enough?

Secondly, i was wondering if it is possible to just install a system 1 to my MBR and in the future when family size increases we just add another set of aircon for the 2 common bedrooms?

I understand the Daikin Smile series allow expansion by just adding FCU but wondering if there will be complication when it comes to expansion?

Or maybe install a system 1 and in the future add another outdoor unit for 2 common rooms?

Appreciate your advices. Thanks!
 
Status
Not open for further replies.
Important Forum Advisory Note
This forum is moderated by volunteer moderators who will react only to members' feedback on posts. Moderators are not employees or representatives of HWZ Forums. Forum members and moderators are responsible for their own posts. Please refer to our Community Guidelines and Standards and Terms and Conditions for more information.