IMDA COPIF documents got specify what kind of connectivity a flat should have. I don't think coaxial is mandated after COPIF 2013.
IMDA COPIF website
https://www.imda.gov.sg/regulations...or-info-communication-facilities-in-buildings
COPIF 2018
https://www.imda.gov.sg/-/media/imd...tations/consultation-papers/11/copif-2018.pdf
COPIF 2018 still has the following clause.
7.10 Provision of telecommunication wiring
7.10.1 Every residential unit shall be provided, at the minimum, with –
(a) RG6 coaxial cable(s) of a number equal to the total number of living room(s)
and bedroom(s), which shall terminate into the output of a multi-way splitter
(which may be located in the utility room or closet) at one end and into an
Ftype TV outlet in each of the living room(s) and bedroom(s) at the other end.
The RG6 coaxial cable(s) shall be provided in accordance with the
requirements set out in chapter 14;
(b) 1 RG6 coaxial cable, which shall terminate into the input of the splitter (which
may be located in the utility room or closet) at one end, and into an IEC 61169-
2 coaxial connector in the living room. This RG6 coaxial cable and IEC 61169-
2 coaxial connector shall be located at the opposite wall of the TV outlet
described in paragraph 7.10.1 (a), and shall be near a window, to enable the
installation of an indoor antenna.8 The RG6 coaxial cable shall be provided in
accordance with the requirements set out in chapter 14; and
(c) unshielded twisted pair cable(s) (Category 6 or better) complying with TIA 568-
C specifications of a number equal to the total number of specified location(s)
within the residential unit, as set out in Table 7.10.1 below, which shall terminate
into an RJ45 patch panel (which may be located in the utility room or closet) at
one end, and into an RJ45 outlet in each of the specified location(s) at the other
end within the residential unit. The length of each unshielded twisted pair cable
shall not exceed 90m.
Table 7.10.1 Number of unshielded twisted pair cable(s) to be provided Location
within residential unit
Number of unshielded twisted pair cable(s) (Category 6 or better) per location
Living room 2
Master bedroom 2
Kitchen 1
Bedroom(s) 1