I mentioned before why some building management agents should not be cutting cost on the filters used in the AHUs. This is to prevent things like sick building syndrome. Also somewhat effective for haze; to lower PM2.5 concentration levels.
Some general knowledge on Building IAQ/Indoor Air Quality ratings and how they achieve it.
EN 13779 - Camfil
•In a city environment, it is recommended to use a molecular filter (gas filter). It is also a good solution in an area of categories ODA 3. The gas filter should be combined with a downstream F8 or F9 particulate filter.
•For hygienic reasons, it is recommended to use two-stage particle filtration:
- Minimum M5, but preferably F7 in the first step.
– Minimum F7, but preferably F9 in the second step.
– If there is only one filtration step, the minimum requirement is F7.
As mentioned before, it goes like this. F7, F8 and then F9.
EN779:2012 - AAF International - Better Air is our Business
Then H10 (Sharp A28), H11 (Novita NAP-101), H12 (some vacuum cleaner exhaust filter).
Then H13 and H14, which are true HEPA
U15, U16 and U17
Some general knowledge on Building IAQ/Indoor Air Quality ratings and how they achieve it.
EN 13779 - Camfil
•In a city environment, it is recommended to use a molecular filter (gas filter). It is also a good solution in an area of categories ODA 3. The gas filter should be combined with a downstream F8 or F9 particulate filter.
•For hygienic reasons, it is recommended to use two-stage particle filtration:
- Minimum M5, but preferably F7 in the first step.
– Minimum F7, but preferably F9 in the second step.
– If there is only one filtration step, the minimum requirement is F7.
As mentioned before, it goes like this. F7, F8 and then F9.
EN779:2012 - AAF International - Better Air is our Business
Then H10 (Sharp A28), H11 (Novita NAP-101), H12 (some vacuum cleaner exhaust filter).
Then H13 and H14, which are true HEPA
U15, U16 and U17